Is there a different calc for sizing though and J-boxes? For example a 2 meter service is fed underground from the utility transformer with 350 kcmil and splices in a horizonal trough with 3/0 thru a nipple to each meter above the trough. Does this need to follow the straight pull rule (314.28A1) or is it different because it is spliced? It would need about a 24" box if that rule is followed, yet most situations I see like this are trough. Is there an exception if it is spliced? Thanks Scott