xtronik
- Hanover, PA
- Electrician, Project Manager
Hello,
I'm sizing a UPS to maintain power during power blips from monthly generator load tests.
The power blip shuts down the Boiler which requires manual intervention to bring it back online.
Boiler is fed by a VFD (480v / 3-phase) that's fed from 400-amp breaker.
The Boiler spec states minimum circuit ampacity is 198.3a.
Using 1.2 - 1.5 as the multiplier for surges: 480 x 198.3 x 1.73 = 164,668kVA (x 1.2 = 197,602kva) (x 1.5 = 247,002kva)
Using the feeder breaker size: 480 x 400 x 1.73 = 332,160kva (x 1.2 = 398,592kva) (x 1.5 = 498,240kva)
The UPS will only need to carry load for 1-2 seconds for the ATS to switch to generator power, with 10-seconds mandatory, a 15-second target would be a good buffer if possible. I'm not sure of the minimum length of battery backup time a UPS can be set up for, except for watt hours and amp hours.
To get 15-seconds of WH (with the highest kVA), I did 1/60 x 1/4 x 498,240 = 2,076wh
To get 15-seconds of AH, I did 1/60 x 1/4 x 198.3 = 0.83ah
Any input on correct calculation?
Where in the code would be a good source for this?
Thanks
Thanks