A client EE sent me an Excel spreadsheet where he has columns for each phase. The panelboard is 3-phase 208V but all loads are 120 single phase (single pole) loads. At the bottom of the spreadsheet he adds up the Amps for each phase which in the above cells of each phase column he was calculating by the consumer kW divided by the product of (voltage x (SQRT of # of Phases) x PF x Eff). For a one pole example that would be 0.6kW / (120V x SQRT(1) x 0.8 x 1.0). Now to clarify, he is applying a 0.8 Power Factor because this panelboard (PB) is deriving its power from an engine-generator set onboard a ship.
So now at the bottom of each phase column he then applies a "loading factor" as he calls it (most on this forum refers to it as Demand Factor). In the next cell below each he than coverts to W, (although in the spreadsheet the label reads "kW". He then adds up three phases for "Total kW". He then applies what he calls a "60% maximum usage" which I would define as design margin or contingency by dividing the Total kW by 0.6 to come up with what he calls "Minimum UPS Rating (kW)". I will in a separate future post the issue of UPS rating in KVA versus Load Analysis such as this in KW rating this equipment's PF & Eff considerations which comes up in design discussions often.
My question is whether his calculating method correct? From prior posts I have seen from fellows, the general consensus is when take this approach you still need to total based on KW rather than Amps because you have PB's that are not balanced per phase circuits. If you do follow this equation would you then apply the three phase factor and divide his total by 1.732 to get the minimum rating on a 3-phase power-rated UPS?
So now at the bottom of each phase column he then applies a "loading factor" as he calls it (most on this forum refers to it as Demand Factor). In the next cell below each he than coverts to W, (although in the spreadsheet the label reads "kW". He then adds up three phases for "Total kW". He then applies what he calls a "60% maximum usage" which I would define as design margin or contingency by dividing the Total kW by 0.6 to come up with what he calls "Minimum UPS Rating (kW)". I will in a separate future post the issue of UPS rating in KVA versus Load Analysis such as this in KW rating this equipment's PF & Eff considerations which comes up in design discussions often.
My question is whether his calculating method correct? From prior posts I have seen from fellows, the general consensus is when take this approach you still need to total based on KW rather than Amps because you have PB's that are not balanced per phase circuits. If you do follow this equation would you then apply the three phase factor and divide his total by 1.732 to get the minimum rating on a 3-phase power-rated UPS?