- Chapmansboro,Tn.
Do you size the branch circuit conductor for a soft start at 125%.
125% of what?
Let's put it this way, sizing conductors for motors controlled by soft starters is no different than sizing them for any motor controller, except VFDs. So you can't size it for less than 125% of the motor FLA from the NEC chart. You can size it for more if you like though...
VFDs are the only type of AC (squirrel cage induction) motor controller that has special rules for conductor and OCPD sizing, and that is just 125% of the VFD Max Amp Rating, not the motor connected to it.
Looks like it to me, a lot of people get confused on the difference. The VFD circuit sizing rules were added in the 2005 NEC, and changed again in 2008, so forsome this is still relatively new. Many people tend to over apply new rules for a while.... I think he is getting confused with a VFD.
VFDs are the only type of AC (squirrel cage induction) motor controller that has special rules for conductor and OCPD sizing, and that is just 125% of the VFD Max Amp Rating, not the motor connected to it.