I have a situation where the condensing unit manufacturer is stating that the MOCP is 100 amp breaker and the MCA is 62 amps. What is the correct wire size?
I understand you take the FLA and mulitple it by 1.25% which gives you the MCA (minimum circuit ampacity) = #6 wire. But is there something in the code that states you can only be within one wire size of your protection and that #4 wire will be required and not #6.
Thanks guys for the help
I understand you take the FLA and mulitple it by 1.25% which gives you the MCA (minimum circuit ampacity) = #6 wire. But is there something in the code that states you can only be within one wire size of your protection and that #4 wire will be required and not #6.