N nicknorth Senior Member Nov 9, 2005 #1 Some showed me a simple way of finding out what size of wire you needed for distances? Here's what I have 8amp load of a distance 800 ft. Does anybody have a quick simple short cut?
Some showed me a simple way of finding out what size of wire you needed for distances? Here's what I have 8amp load of a distance 800 ft. Does anybody have a quick simple short cut?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Nov 9, 2005 #2 Re: sizing wire on distance real simple answer.. go to Bussmann.com and download their software for voltagedrop.
Re: sizing wire on distance real simple answer.. go to Bussmann.com and download their software for voltagedrop.
N nicknorth Senior Member Nov 9, 2005 #3 Re: sizing wire on distance I looked on bussmann and I don't see where the voltage drop software is? Could you point it out for a blind guy?
Re: sizing wire on distance I looked on bussmann and I don't see where the voltage drop software is? Could you point it out for a blind guy?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 9, 2005 #4 Re: sizing wire on distance Try this calculator: http://www.electrician.com/vd_calculator.html
S sparky59 Senior Member Nov 10, 2005 #6 Re: sizing wire on distance #4awg copper would get you a 3.2% vd.