Hello,
I am confused on how to calculate the Circular Mils to determine the size of the wires for a commercial lighting circuit on the outside of a Storage Unit building.
I have seven 120 Volt LED lights with Drivers that draw 1.2 amps each. The total amperage draw is 8.4 amps. It is a continuous load and must be increased 125% for 10.5 amps. I will install a 20 amp circuit.
The lights are equally spaced. The furthest light is 370 feet away. I want no more than three percent voltage drop on the branch circuit.
I am aware of the CM formula, just not sure which amperage value to use.
Question: Do I calculate the size (CM) of the wire based on 1.2 amps, or 8.4 amps, or 10.5 amps at 370 feet?
Thank you for your time.
I am confused on how to calculate the Circular Mils to determine the size of the wires for a commercial lighting circuit on the outside of a Storage Unit building.
I have seven 120 Volt LED lights with Drivers that draw 1.2 amps each. The total amperage draw is 8.4 amps. It is a continuous load and must be increased 125% for 10.5 amps. I will install a 20 amp circuit.
The lights are equally spaced. The furthest light is 370 feet away. I want no more than three percent voltage drop on the branch circuit.
I am aware of the CM formula, just not sure which amperage value to use.
Question: Do I calculate the size (CM) of the wire based on 1.2 amps, or 8.4 amps, or 10.5 amps at 370 feet?
Thank you for your time.