Cow
Senior Member
- Location
- Eastern Oregon
- Occupation
- Electrician
Just an example, for a 100HP 480v pump panel with a 250 amp main breaker, the service entrance wire is sized to the motor charts, correct? Regardless of the breaker size?
I'm looking at 230.42(A) and (A)(1). So a 100HP motor gives us 124A x 125%=155 amps. 2/0 wire? Thanks.
I'm looking at 230.42(A) and (A)(1). So a 100HP motor gives us 124A x 125%=155 amps. 2/0 wire? Thanks.