Sizing wireway

Status
Not open for further replies.

vortiz.08

Member
Location
Dallas Texas
So I have 8 #250 in (2) 2 1/2” I need a wireway plus I need to splice In the wireway I’m also going from 250 aluminum to 3/0 copper just trying to understand this better
 

MattS87

Senior Member
Location
Yakima, WA
So I have 8 #250 in (2) 2 1/2” I need a wireway plus I need to splice In the wireway I’m also going from 250 aluminum to 3/0 copper just trying to understand this better

You would use art. 376.23 and 314.28 to size it. Wires larger than #4 require the 6 or 8 multiplier based on conduit size. You multiply your largest conduit size by 6 or 8 depending straight or angled pulls, then add all of your other conduits (2.5x8=20+2.5 =22.5). So one of the dimensions of your wireway would have to be greater than or equal to 22.5"
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There is no need to add the extra conduit sizes on a straight pull. It's simply 8X the largest conduit size.
 

MattS87

Senior Member
Location
Yakima, WA
But I will have splices in this how do I calculate that

May be wrong here but you don't need to calculate for splices. Using the multiplier (6 or 8) times the largest conduit will take this into account. Box fill is only used with conductors smaller that #4
 

kwired

Electron manager
Location
NE Nebraska
May be wrong here but you don't need to calculate for splices. Using the multiplier (6 or 8) times the largest conduit will take this into account. Box fill is only used with conductors smaller that #4
376.22(A) says 20 percent fill for the contained conductors

376.56(A) says the conductors and splices can't fill any cross section more then 75 percent. So the splicing method will make some difference - though staggering splices so they are not all at same cross section will help with that.
 

MattS87

Senior Member
Location
Yakima, WA
376.22(A) says 20 percent fill for the contained conductors

376.56(A) says the conductors and splices can't fill any cross section more then 75 percent. So the splicing method will make some difference - though staggering splices so they are not all at same cross section will help with that.

Good to know. So per the OP's question, how would you calculate how much fill the splices take up? Based on splice method?
 

kwired

Electron manager
Location
NE Nebraska
Good to know. So per the OP's question, how would you calculate how much fill the splices take up? Based on splice method?
Absolutely based on splice method. Crimped butt splice type devices typically won't take up as much room as Polaris connectors or similar.

conductor fill probably isn't too much issue, especially if entering with raceways at the "ends", as the wireway has to be larger then the raceway(s) just to terminate into the wireway. If running 2 -2.5 inch raceways into an end - you probably need at least 8 inch by 4 inch wireway - presuming that is something available 8x8 is probably something more common though and would have quite a bit of room for splicing - still may want to stagger splices to some extent especially with terminal blocks or polaris connectors.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you keep your fill below 20% IMO it's nearly impossible to exceed 75% with the splices.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
If you keep your fill below 20% IMO it's nearly impossible to exceed 75% with the spices.
Depends on the spice method, and maybe whether or not you put all spices in same cross section.

My spices are all in a cabinet close to the range, not sure what the fill is.:D
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Fixed it. I'll go out on a limb and say that there is probably no splicing method that will occupy more than 75%.
 