Strathead
Senior Member
- Location
- Ocala, Florida, USA
- Occupation
- Electrician/Estimator/Project Manager/Superintendent
When a conductor enters the end of a wireway and exits the side similar to and LR or LL conduit body, does 312.6A apply? If not, then what does? I am reading 314.28 (A)(2) and it seems that that installation is not legal. The width of the wireway must be 6 times the diameter of the conduit. And I would guess that an LL or LR is acceptable only because it has a listing is this correct? The only time the 312.6A can be used is when you are entering opposite the cover.
"(2) Angle or U Pulls, or Splices. Where splices or where angle
or U pulls are made, the distance between each raceway entry
inside the box or conduit body and the opposite wall of the
box or conduit body shall not be less than six times the metric
designator (trade size) of the largest raceway in a row. This
distance shall be increased for additional entries by the amount
of the sum of the diameters of all other raceway entries in the
same row on the same wall of the box. Each row shall be calcu‐
lated individually, and the single row that provides the maxi‐
mum distance shall be used.
Exception: Where a raceway or cable entry is in the wall of a box or
conduit body opposite a removable cover, the distance from that wall to
the cover shall be permitted to comply with the distance required for one
wire per terminal in Table 312.6(A).
The distance between raceway entries enclosing the same
conductor shall not be less than six times the metric designator
(trade size) of the larger raceway."
"(2) Angle or U Pulls, or Splices. Where splices or where angle
or U pulls are made, the distance between each raceway entry
inside the box or conduit body and the opposite wall of the
box or conduit body shall not be less than six times the metric
designator (trade size) of the largest raceway in a row. This
distance shall be increased for additional entries by the amount
of the sum of the diameters of all other raceway entries in the
same row on the same wall of the box. Each row shall be calcu‐
lated individually, and the single row that provides the maxi‐
mum distance shall be used.
Exception: Where a raceway or cable entry is in the wall of a box or
conduit body opposite a removable cover, the distance from that wall to
the cover shall be permitted to comply with the distance required for one
wire per terminal in Table 312.6(A).
The distance between raceway entries enclosing the same
conductor shall not be less than six times the metric designator
(trade size) of the larger raceway."