sizzling sockets batman

Status
Not open for further replies.

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor
any idea why these sockets after these workhorse ballasts should be failing in record numbers?

photo.jpg
it is the workhorse 5 and two f54 lamps

nominal 120v

the fixtures are pretty well enclosed.

I'll do some thermal imaging later this week.

The ballasts were never screwed into the enclosure. Apparently they were glued in at the factory.

Some of the fixtures are on dimmers, but I can't believe that there are any workhorse ballasts in there.
I haven't taken the fixtures after the dimmers apart yet.

Some sockets had loose wires, but that could be because... they were melted!

What should I be looking for, what could be overdriving these ballasts, causing such heat at the sockets?

lack of grounding? could that do it?

dimmers... sure

temperature? enclosed fixture

loose wires at the sockets, cheap sockets
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
any idea why these sockets after these workhorse ballasts should be failing in record numbers?

What should I be looking for, what could be overdriving these ballasts, causing such heat at the sockets?

lack of grounding? could that do it?

dimmers... sure

temperature? enclosed fixture

loose wires at the sockets, cheap sockets
Just looking at the photo, I do not see any clear evidence that ballast heat started the whole thing off. Rather that the charring on the ballast housing came from heat at the socket.
If the spring contacts in the sockets lose their elasticity at high temperatures, or have other reasons for reduced contact pressure, that might have been the start of the problem. If the sockets are rated for the type and power lamps used, they should be OK though, as long as the lamp pins were clean at installation and the lamps were installed securely.

Are these sockets the type where you slide a bi-pin base fully into the slot and then rotate 90 degrees to make the connection to the shielded contacts? Is there a noticeable detent at the 90 degree point? If not, the tubes may have been under or over rotated leaving the contact points insecure. Once resistive heating or arcing starts, it will just get worse.
 
Last edited:

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor
just a whole bunch of bad sockets??

just a whole bunch of bad sockets??

yes, the ballasts are still working in the majority of cases.
if the ballasts are just glued in there, could this be a cause of overdriving the sockets
should I tap a hole for the ballasts anyway?

the sockets look just like this
http://semperlite.com/products/lampholders/main.php?PR_ProductID=706

there is no temperature rating i can see there
maybe i will just have to drill a few holes in each fixture...
I would drill thru the UL label but I saw no name or label there:angel:

I've seen lots of trouble w t5 fixtures, but usually the dimming kind.
 

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor
photo(1).jpg
bypass the socket and it works great!
but it looks like it happens on a regular basis.
gotta try drilling some holes in there and grounding the ballast
the old ballast was just glued in there.
 

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor
pigtail

pigtail

might be better to pigtail a wire to each socket rather than shunting thru those cheap springs
http://horse.fulham.com/wiring-diagram-results/

thats where the problem keeps happening, where the yellow starts under the little spring.
looks like i can wire them better in parallel than in series here as long as they are shunted already
 
Last edited: