SkillsUSA preliminary contest Industral Motors Controls Written test Q2

Learn the NEC with Mike Holt now!

SkillsUSA preliminary contest Industral Motors Controls Written test Q2

  • 9x9x1

    Votes: 0 0.0%
  • 8x16x3

    Votes: 0 0.0%
  • 9x24x10

    Votes: 0 0.0%

  • Total voters
    3
Status
Not open for further replies.

fmtjfw

Senior Member
A wall mounted box has an EMT into its left side & down from its bottom. Each contain 10 #4 wires which are spliced in the box. Minimum box size?


Also code references?
 
Last edited:

cpinetree

Senior Member
Location
SW Florida
I went with 9 x 12 x 6

I think you only need 9 x 9 x 3 (2011 NEC 314.28(A)2)

10 - #4 THHN max conductors in an 1 1/2" EMT

1.5" x 6 = 9"

I don't want to be the one pulling it in I would go 1 size larger to 2" EMT and a larger Pull box (12 x 12 x 6) labor is way more expensive than the materials, and why fight it.:)
 

fmtjfw

Senior Member
My Answer

My Answer

B

(2) A wall mounted box has a conduit into its left side & down from its bottom. Each contain 10 #4 wires which are spliced in the box. Minimum box size?

To calculate the box size you need to determine the size of the conduit needed to properly hold 10 #4 conductors. Given the size of the conduit. Since we have angle splice, we multiply by 6 for both length and width.

Table C.1 [70-746] is for EMT. Under type THWN-2 the #4 row, you find that the smallest conduit that will hold 8 conductor is 1? (which holds 10).

You can also do it the hard way with Chapter 9 Table 5 type THWN-2 the #4 row which gives 0.0824 in2 per wire or a total of 0.824 for all wires. The Table contains 0.814 in the 40% column for 1? EMT. Now dividing 0.814/0.824 gives 0.988. According to table note 7 under these circumstances if the division gives 0.8 or higher, the conduit is big enough.

Either way we get 1? conduit. Multiplying that by by 6 gives 9, so the box must be at least 9x9. The depth of the box must be enough for the conduit to fit in the side so the 1 inch deep box can't be used.
The smallest box is 10?12?3 from the list

Code Ref:
Table C.1 OR Chapter 9 tables 3 & 5 and note 7
314.28(A)(2)

Index:
Conduits ? Conductors, number in
Boxes (outlet device, pull, and junction) ? Junction, pull see Junction Boxes
Junction Boxes ? Size ? Conductors 4 AWG and larger
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
But when you are dealing with bending space requirements rather than fill requirements, a box with the same or larger volume but wrong dimensions fails.

Sent from my Droid Maxx
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
But when you are dealing with bending space requirements rather than fill requirements, a box with the same or larger volume but wrong dimensions fails.

Sent from my Droid Maxx
But there is a box on the list that meets the requirements and is much smaller by volume than the one in answer B.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The sizes are random, not out of a catalog.

The sizes are chosen so that the smallest may be by L?W or volume and give the same answer.
There is nothing to say that the box has to have its back mounted to the wall. You could mount the 8x16x3 box on the wall with the opening up and the 16" side against the wall. This box mounted that wall meets the requirements of the code and is smaller in volume than the 9x12x6.
 