What is the number of conductors in a conduit containing a grounding wire, two 3-phase feeders and a neutral?
Also Code References??
I read it to say 2 x 3 +1 +1
I don't know a Code reference for counting
The question might be asking "Number of current carrying conductors"
And that is being tricky!.... The question also states a neutral, which can be shared between the two 3-phase feeders. (and the shared grounding wire) I 've got to be a little tricky:roll:
How did one question turn into two questions?:?
I also think if you want to throw a little trickiness in there you best be accurate with all the details, I would recommend changing "grounding wire" to "equipment grounding conductor" as that is what the NEC calls it, and does a consistent job of referring to it as that, and same goes when talking about the "grounded conductor" though the term neutral is used, it is one of those situations that is a little trickier sometimes and you need to watch the use of those two words and use them in same manner as the NEC does IMO.
The word "conduit" is not foreign to NEC but in the field is a little more of a word just thrown around. NEC generally uses the term "raceway" and the word "conduit" is generally a more specific descriptive word for a particular "raceway" such as "flexible metal conduit" or "rigid metal conduit".
Two alternative ways of clarifying the original question.
OK - EGC not GC.
Raceways / Conduits -- Index entry to find CCC information is in Conduit not in Raceway
the CCC and Conductor Count questions are the same (other than CCC and Count).
100 Neutral Point. The common point on a wye-connection in
a polyphase system or midpoint on a single-phase, 3-wire
system, or midpoint of a single-phase portion of a 3-phase
delta system, or a midpoint of a 3-wire, direct-current system.