skm arc flash calculation

Status
Not open for further replies.

BillPratt58

Member
Location
sioux city,ia
I ran an arc flash study from SKM, electrical system has a MCC with a main 800A fuse. The incident energy is the same on the main fuse as the rest of the MCC. So, im assuming if I had a fault on the MCC bus that the main fuse wouldnt open. Is this assumption correct
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
That is an incorrect assumption.
What it means is that whether the fuse opens or not the upstream current limiting and protection will still limit the incident energy to the same value.


Sent from my XT1585 using Tapatalk
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Or depending on the SKM settings, I think it could also mean that you are looking at the incident energy on the load side of the main fuse in both the main compartment and the other MCC sections.
 

shortcircuit1

Senior Member
Location
USA
I ran an arc flash study from SKM, electrical system has a MCC with a main 800A fuse. The incident energy is the same on the main fuse as the rest of the MCC. So, im assuming if I had a fault on the MCC bus that the main fuse wouldnt open. Is this assumption correct

It would be better if you can show the oneline and what buses you faulted...
 