EngineeringWorker
New User
- Location
- Alberta
- Occupation
- Engineer
There is a cable ampacity module in SKM but something doesn't look right with the results it produces.
I ran a multitude of cable ampacity studies to create myself 2 tables of values with the same parameters except the thermal resistivity of the duct bank. One of them uses Concrete fill for the ductbank (Thermal resistivity = 65Rho) and the other uses Very Dry Soil/Sand (Thermal resistivity = 120Rho) for the ductbank fill.
Given that the higher the thermal resistivity, the harder it is for heat to transfer away from the material, here's what I'd expect:
Expected:
And generally this holds true for findings at higher cable sizes/runs. But at lower cable sizes/runs, I found the opposite.
Actual:
You can see in the screenshot below the tables of values I've created. The ampacity values from each table should be consistent relative to the other table (ampacity of Concrete should be consistently higher than Sand) but it's actually inconsistent.
I've asked SKM Helpdesk on this, for an explanation on what is going wrong, and was only told it is normal to get less ampacity with Sand backfill, and more ampacity with Concrete backfill. Followed up to get a clarification with the above table of values, haven't heard back but it's only been 2 days so I might have to be more patient. Anyone else understand what's causing this inconsistency?
I ran a multitude of cable ampacity studies to create myself 2 tables of values with the same parameters except the thermal resistivity of the duct bank. One of them uses Concrete fill for the ductbank (Thermal resistivity = 65Rho) and the other uses Very Dry Soil/Sand (Thermal resistivity = 120Rho) for the ductbank fill.
Given that the higher the thermal resistivity, the harder it is for heat to transfer away from the material, here's what I'd expect:
Expected:
| Duct Bank Material | Soil Resistivity (C-cm/W) | Cable Ampacity | Conductor Temperature |
| Concrete | 65 | Higher than Sand’s | Lower than Sand’s |
| Sand | 120 | Lower than Concrete’s | Higher than Concrete’s |
Actual:
| Duct Bank Material | Soil Resistivity (C-cm/W) | Cable Ampacity | Conductor Temperature |
| Concrete | 65 | Lower than Sand’s | Higher than Sand’s |
| Sand | 120 | Higher than Concrete’s | Lower than Concrete’s |
I've asked SKM Helpdesk on this, for an explanation on what is going wrong, and was only told it is normal to get less ampacity with Sand backfill, and more ampacity with Concrete backfill. Followed up to get a clarification with the above table of values, haven't heard back but it's only been 2 days so I might have to be more patient. Anyone else understand what's causing this inconsistency?