Desert Spark
Member
- Location
- New Mexico
I'm running a new service to a well house that is a pre-fabbed, tough shed type structure, about 8' x 12', 2x4 framing.
I was sent to the job after the slab was poured and the shed already in place. The approved plans I was given called for a concrete encased electrode with 20' of #4 copper encased. Since we were on site after the fact I just went ahead and drove two ground rods.
It's about a 4" slab with no footing, poured on a gravel base. Would a CEE even be acceptable in this situation? The code says metallic components must be located horizontally in a foundation or footing in direct contact with earth.
I was browsing through some other posts on grounding electrodes and discussions on if they are available you have to use them and made me think of this. I don't know if the inspector will say that the ground rods are not on the prints and why wasn't the ufer installed, but I was just trying to see that if he did, I could simply say that the slab doesn't meet the requirements anyway.
Also on the topic, what if you arrive on a job that meets all the parameters for having a CEE, but there is not copper ran or rebar stubbed up to make the connection? Say someone put up a metal building and then hired an EC later and there was not a chance to get it done. Does that mean that the CEE exists, and you have to somehow make the connection, or could it fall under the exception for existing buildings or structures?
Thanks for any info.
I was sent to the job after the slab was poured and the shed already in place. The approved plans I was given called for a concrete encased electrode with 20' of #4 copper encased. Since we were on site after the fact I just went ahead and drove two ground rods.
It's about a 4" slab with no footing, poured on a gravel base. Would a CEE even be acceptable in this situation? The code says metallic components must be located horizontally in a foundation or footing in direct contact with earth.
I was browsing through some other posts on grounding electrodes and discussions on if they are available you have to use them and made me think of this. I don't know if the inspector will say that the ground rods are not on the prints and why wasn't the ufer installed, but I was just trying to see that if he did, I could simply say that the slab doesn't meet the requirements anyway.
Also on the topic, what if you arrive on a job that meets all the parameters for having a CEE, but there is not copper ran or rebar stubbed up to make the connection? Say someone put up a metal building and then hired an EC later and there was not a chance to get it done. Does that mean that the CEE exists, and you have to somehow make the connection, or could it fall under the exception for existing buildings or structures?
Thanks for any info.