Here is the layout,
Voltage: all the common voltages up to 480/277
Amperes: as in panel size 100a-400a and larger, MCB or MLO
Here's the deal, a lighting contactor is nippled to any of the above, let's
say six circuitsare controlled. The Inspectors are requiring us to either
loop 10' of the branch circuit conductors in the panel or run 10' of pipe
to a j-box and then back down to the LCC instead of using a nipple.
The Inspectors can't really explain to me why, but they are just doing
their job. It has something to do with the circuit needs enough resistance
to trip the c.b.?
This has been bugging me for awhile, If anyone can explain this to me,
I be your slave for life!!