sleaving NM cable thru conduit

Status
Not open for further replies.
is it permissible to sleave nm cable(S) thru conduit?
i am getting mixed info from my co-workers with no NEC reference
an answer with an article referance would be greatly appreciated
-cheers
 

resistance

Senior Member
Location
WA
Yes its ok, but for indoor use only (NM cable is not allowed in wet or damp locations). Conduit fill must be considered. Heres one that makes it clear: NEC 334.15 (B) Note: I’m rusty
 
Last edited:
NM through conduit

NM through conduit

The code states that when transferring from one wiring method to another you must use a J Box unless a UL approved fitting is used Check out Bridgeport Fittings # 280-DC This will allow for nm to 1/2 EMT
 