IS there code as to when you need to sleeve and firestop for electrical conduits? Is it always through fire rated walls?
Thanks.
Thanks.
Fire stopping is another set of codes outside the NEC - UBC,IBC or whatever is applicable to your AHJ...IS there code as to when you need to sleeve and firestop for electrical conduits? Is it always through fire rated walls?
Thanks.
Not alot of plans will show - or even identify rated assembelies unless the AHJ has required it to be done and/or submitted.The plans should identify the UL assembly to be used then you need to follow the details for that assembly.
Not alot of plans will show - or even identify rated assembelies unless the AHJ has required it to be done and/or submitted.
Even though I am most often just handed the E sheets alone... Many times you would be hard pressed to locate in the rest of it. Certain places are more on the ball about requiring that information than others, and some base it only on the rating of the building - requiring that info of some, but not others... Commercial but ignore residential... :roll: