Why and were are sleeves used. I know you fireproof when passing through a fire rated wall but you don't need to use a sleeve.

EDIT-------Disregard post, thanks.
 
Most gc's want you to use a sleeve were you have multiple wire assembles penetrating a fire rated wall.

it makes it easy for them to fill the sleeve with fire caulk we usually fill 3" conduit to 60percent.
 
Why and were are sleeves used. I know you fireproof when passing through a fire rated wall but you don't need to use a sleeve.

EDIT-------Disregard post, thanks.

In many cases sleeves through walls are not required but for some reason designers want them. Sleeves installed in pored concrete are a different story.
 