Sleeves through Concrete wall underground

Status
Not open for further replies.
Does anybody have experience installing conduit sleeves in a concrete form underground. For example 6" rigid sleeve for 4" PVC through wall. I need to make sure they are level and straight and I intend to "sandwich" them between the forms using 3/8" threaded rod, 4s blank with KO on each side of the form and square washers and nuts to squeeze it all together. I haven't performed this task before and I'm looking to see if anybody has more clever procedure. The conduits will be suspended above ground.
 
If this is underground you may need a sleeve with a water stop if this is going to be link sealed.
Otherwise it may leak around the outside of the sleeve.
 