Sleeving romex

Status
Not open for further replies.

DonBos

Member
Does the NEC Code allow for sleeving romex in ENT, PVC, or metal pipe for
a distance more than 8"? What code reference would it be? I am being
told by the inspector that there is a heat risk.
 
DonBos said:
Does the NEC Code allow for sleeving romex in ENT, PVC, or metal pipe for
a distance more than 8"? What code reference would it be? I am being
told by the inspector that there is a heat risk.


Art. 334.15(B) permits sleeving wires in conduit as does art.312.5(C). You just have to watch for derating and conductor fill.
 