Can you sleeve UF in 3/4" emt in and out of a 2nd floor deck down to switch boxes and recep boxes below? Providing bushings or emt/nm connectors of course.
I think UF is allowed for underground use; when it emerges from underground it is in a conduit. Also, I believe you can also use UF in dry locations where NM is used, it is just darn hard to strip. I think there is no cable that is allowed on or under a deck.
What article can you support that statement withI think there is no cable that is allowed on or under a deck.
I think UF is allowed for underground use; when it emerges from underground it is in a conduit. Also, I believe you can also use UF in dry locations where NM is used, it is just darn hard to strip. I think there is no cable that is allowed on or under a deck.
Disagree, except for the hard to strip (in comparrison to NM).
The newer UF is pretty easy to strip, I use my klines 14-2 12-2 strippers and it slides off with ease..... If its difficult to strip, you're doing it wrong.
Or, it's winter and you left it in the van overnight.
Yeah, I try not to use UF in the winter, because that usually involves being outside.
I had some 2/0 THHN/W split on me once. We got the inside done and had about 5 feet left outside to do and went to lunch. When we got back and I tried to get the 2/0 through the LB, the insulation split like it was glass. I think it was 9 degrees or so.