Sloping Duct Pipes

Status
Not open for further replies.

vidividi12

Member
Location
San Marino
Occupation
Electrician
Hi,

We will put sch40 underground ductbank pipes to connect A building to B building. Also, it is mentioned in our specifications that "Conduits shall be sloped to drain toward manholes at a minimum rate of 1:300." However, in our plan, pipes are going through from A building through B building. There is not any handhole and manhole for duct sloping. How can I make a slope without manhole or handhole?
 

masterinbama

Senior Member
Hi,

We will put sch40 underground ductbank pipes to connect A building to B building. Also, it is mentioned in our specifications that "Conduits shall be sloped to drain toward manholes at a minimum rate of 1:300." However, in our plan, pipes are going through from A building through B building. There is not any handhole and manhole for duct sloping. How can I make a slope without manhole or handhole?
Looks like a generic specification. Submit a change order to add the previously undocumented manhole.

Sent from my LML211BL using Tapatalk
 