SMA CORE1 90C TERMINALS

Status
Not open for further replies.

310 BLAZE IT

Senior Member
Location
NJ
You heard it here first... It's clearly written in their installation manual (I got an early copy) This is a huge deal if it means we can use this column. I know this has been covered a million times but I've never seen a product actually listed for 90C until now
cc5f1e54d619c1117f82e710e2ac4ce8.jpg


Sent from my SM-N920V using Tapatalk
 
I know breakers aren't allowed to be 90C at 100A Per NEC But just seeing what people's thoughts are.

Sent from my SM-N920V using Tapatalk
 
I know breakers aren't allowed to be 90C at 100A Per NEC But just seeing what people's thoughts are.

Sent from my SM-N920V using Tapatalk
I don't think NEC prohibits 90C rating, it is just rare to find it, especially on a typical thermal-mag breaker.

Whatever equipment you have there may have 90C terminals, but if you run a 90C conductor directly to a circuit breaker, that breaker likely has 75C terminations - so you still need to connect conductors sized per 75C ampacity columns to the breaker. You could change conductor size before landing on your equipment though, with a 90C splicing method.
 
The AC Conductors are permissible at 90 deg in the device you have, but you still will size the ampacity to 60 or 75 deg based on its size (<>100A) and cable type.

The wires in many fixtures indicate 90 deg wires required, but the ampacity would still be 60 or 75 deg.
 