electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
- Occupation
- Electrician
This is my first time commissioning a SMA inverter so I am a bit unsure of everything. Just want to get a sanity check on if there is something obvious I am missing before I call SMA. I have two SB7.0 connected to a 120/240 split phase system. System does go thru two transformers before getting to the utility and I have about 8 volts of "rise" at full load, so I have the transformers taps adjusted to give me 115/230 at the inverter outputs with no current. I confirmed this voltage with my meter and the inverters agree. Seems like this should not be a problem: looking at the specs I see a voltage range @ 240 of 211-264. Only thing I can think of is that is "expecting" a different grid configuration, but I dont recall seeing any such setting in the setup.