Small appliance branch circuit question

cppoly

Senior Member
Location
New York
In addition to the two small appliance branch circuits required to have of a load of 1,500 VA each, two questions about running a dedicated circuit to a specific appliance in the kitchen (as allowed per exception in 210.52(B)(1)):

1) Is this dedicated circuit considered a small appliance branch circuit?

2) Is there a 1,500 VA requirement for this dedicated circuit OR does this dedicated circuit get the specific appliance wattage? For instance, let's say 800 watts for a microwave. Would 1,500 VA or 800 VA be required in the panel?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In addition to the two small appliance branch circuits required to have of a load of 1,500 VA each, two questions about running a dedicated circuit to a specific appliance in the kitchen (as allowed per exception in 210.52(B)(1)):

1) Is this dedicated circuit considered a small appliance branch circuit?

2) Is there a 1,500 VA requirement for this dedicated circuit OR does this dedicated circuit get the specific appliance wattage? For instance, let's say 800 watts for a microwave. Would 1,500 VA or 800 VA be required in the panel?

1) It can be as in a refrigerator but it would not be for a dishwasher. It must be accessible to the kitchen counter.

2)Not sure what you are asking here. Do you mean for calculation purposes
 

cppoly

Senior Member
Location
New York
Thanks.

Yes, for calculations. I'm asking if you choose to run a dedicated circuit in the kitchen (for a refrigerator, microwave, etc.), if this required to be considered a SABC with a 1,500VA load OR is this load specific to the appliance (400 watts, 800 watts, etc.)? In other words, for each dedicated circuit you run to a specific receptacle, does each load need to be 1,500VA or only the load of the appliance?

Here's the exception I'm referring:

210.52(B)(1)

Exception No. 2:
In addition to the required receptacles specified by 210.52, a receptacle outlet to serve a specific appliance shall be permitted to be supplied from an individual branch circuit rated 15 amperes or greater.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
A dedicated circuit for a specific load need not be a SABC. it is counted at its rated load. It can even be a 15 amp circuit, as the exception you cited clearly states.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
If the dedicated circuit was a receptacle that landed on the kitchen counter and was able to be utilized by other appliance then it would be calculated at 1500 VA.
Partially disagree--if the receptacle is in addition to the required 2'/4' receptacles, then you can declare the dedicated circuit not an SABC (whether it is 15A or 20A or more), and count it according to the rating of the intended load.

Cheers, Wayne
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Wayne, I need to disagree with you on this point. 210.11(C)(1) calls for two or more small appliance branch circuits. 210.52(B)(1) says those two or more shall serve all kitchen countertop receptacles.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Partially disagree--if the receptacle is in addition to the required 2'/4' receptacles, then you can declare the dedicated circuit not an SABC (whether it is 15A or 20A or more), and count it according to the rating of the intended load.

Cheers, Wayne
Where is that wording? If it lands on the counter, IMO it is counted as 1500. unless direct wired
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Wayne, I need to disagree with you on this point. 210.11(C)(1) calls for two or more small appliance branch circuits. 210.52(B)(1) says those two or more shall serve all kitchen countertop receptacles.
But 210.52(B)(1) has an exception, as quoted in post #3. So if we use an individual branch circuit to serve a specific appliance, even on the countertop, then that branch circuit need not be an SABC (indeed, it is allowed to have only 15A OCPD, which is not allowed for an SABC).

Cheers, Wayne
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Where is that wording? If it lands on the counter, IMO it is counted as 1500. unless direct wired
210.52(B)(1) Exception 2, as quoted in post #3. That's an exception to the 210.52(B)(1) language that "the two or more" SABCs "shall serve . . all countertop outlets covered by 210.52(C)." It lets us put a countertop outlet on an individual branch circuit for a specific appliance.

Cheers, Wayne
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
210.52(B)(1) Exception 2, as quoted in post #3. That's an exception to the 210.52(B)(1) language that "the two or more" SABCs "shall serve . . all countertop outlets covered by 210.52(C)." It lets us put a countertop outlet on an individual branch circuit for a specific appliance.

Cheers, Wayne
So how does one define that circuit, as a receptacle, only for an appliance. It is all moot because the difference in the calculation will probably not be enough to worry about.

I agree with what you said. I read the exception in 210.52 and read 220.52 as 210.52(B)(10)
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
So how does one define that circuit, as a receptacle, only for an appliance.
Well, on the plans it will show as for a specific appliance, and the load calc would include the load of that appliance. And in the field, it will be installed as an individual branch circuit, which likely means the circuit has only one outlet (although that is not required).

Cheers, Wayne
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
So you guys would conclude if not to serve the counter top it would not need GFCI protection unless 6 ft from the sink?
The language in 210.8 has changed recently. In the 2023 NEC 210.8(A)(6) just says "kitchens" and so would apply regardless.

In the 2020 NEC, it says "kitchens--where the receptacles are installed to serve the countertop surfaces." That is not necessarily synonymous with being a 210.52(C) receptacle on an SABC. I think that language would also cover a receptacle on an individual branch circuit to serve a specific appliance that lives on the countertop surface, if the appliance is not fixed in place.

Cheers, Wayne
 

david

Senior Member
Location
Pennsylvania
The language in 210.8 has changed recently. In the 2023 NEC 210.8(A)(6) just says "kitchens" and so would apply regardless.

In the 2020 NEC, it says "kitchens--where the receptacles are installed to serve the countertop surfaces." That is not necessarily synonymous with being a 210.52(C) receptacle on an SABC. I think that language would also cover a receptacle on an individual branch circuit to serve a specific appliance that lives on the countertop surface, if the appliance is not fixed in place.

Cheers, Wayne
I think from a liability point i would agree but the language in 2020 doesnt seem to suport that " countertop surfaces'
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
And in the field, it will be installed as an individual branch circuit, which likely means the circuit has only one outlet (although that is not required).
I believe it is required. By definition, an individual branch circuit serves only one utilization equipment.
 