If I have more than 2 receptacle circuits in a residential kitchen (counter top) do I have to calculate the extra circuits at 1500VA each? What if I have 2 separate circuits in the kitchen (counter top) and one or more in the dining room? Do I have to include the dining room circuit at 1500VA just because its in the dining room? Or can those receptacles be covered by the 3VA/sq. ft. calc? I guess I'm basically asking is there ever a time when you include more than the 2 required 1500VA small appliance branch circuits in a calc?
Also, if I have 2 circuits of kitchen (countertop) receptacles that I'm counting as my 2 1500VA small appliance circuits and I have a dedicated circuit with a single recepatcle for a refrigerator (in the kitchen) do I have to count that refrigerator receptacle as another 1500VA small appliance branch circuit?
Do you usually include a standard plug and cord connected refrigerator in your permanently connected appliance load calc? What about a standard cord and plug connected mircowave? I would assume these loads are covered under the small appliance branch circuits calcs or the 3VA/sq. ft. but I'm not positive.
Also, if I have 2 circuits of kitchen (countertop) receptacles that I'm counting as my 2 1500VA small appliance circuits and I have a dedicated circuit with a single recepatcle for a refrigerator (in the kitchen) do I have to count that refrigerator receptacle as another 1500VA small appliance branch circuit?
Do you usually include a standard plug and cord connected refrigerator in your permanently connected appliance load calc? What about a standard cord and plug connected mircowave? I would assume these loads are covered under the small appliance branch circuits calcs or the 3VA/sq. ft. but I'm not positive.