small appliance ckt. & arch-fault protection

Status
Not open for further replies.

Buckaroo

Member
According To 210.52(b)(1) The Two Or More Appliance Circuit Shall Serve All Wall And Floor Receptacles In The Kitchen, Pantry, Breakfast Room, Dining Room Or Similar Area.

Then According To 210.12(b) All 15amp And 20amp Branch Circuits Supplying Outlets In Family Room, Dining Rooms, Living Rooms, Parlors, Libraries Dens, Bedroom, Sunrooms, Recreation Rooms, Closets, Hallways Or Similar Rooms Shall Be Arch Fault Protected.

So?.the 2 Appliance Circuits Have To Be Arch Fault Protected Correct Because They Serve The Dining Room?
 
Buckaroo said:
According To 210.52(b)(1) The Two Or More Appliance Circuit Shall Serve All Wall And Floor Receptacles In The Kitchen, Pantry, Breakfast Room, Dining Room Or Similar Area.

Then According To 210.12(b) All 15amp And 20amp Branch Circuits Supplying Outlets In Family Room, Dining Rooms, Living Rooms, Parlors, Libraries Dens, Bedroom, Sunrooms, Recreation Rooms, Closets, Hallways Or Similar Rooms Shall Be Arch Fault Protected.

So?.the 2 Appliance Circuits Have To Be Arch Fault Protected Correct Because They Serve The Dining Room?

I generally run a 3rd appliance circuit for the dining room etc... ;) But you are correct.
 