I have an apartment building that is upgrading appliances originally they spec'ed a separate microwave and exhaust hood, I interpreted the microwave load to be on the small appliance branch circuit and the exhaust hood not to be. They just changed that to a combined unit (GE JVM3160) to be mounted above the range, the unit is cord and plug, 120v, 15a. I am wondering if I can count this under the small appliance load. Please provide NEC 2011 references that apply.
Coppersmith
Tampa, FL, USA
Electrical Contractor
422.16(B)(4)Range Hoods.
Range hoods shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for use on range hoods in the installation instructions of the appliance manufacturer, where all of the following conditions are met:
(5) the receptacle is supplied by an individual branch circuit.
Why, you ask, should a hood require a separate circuit? I'm assuming it's because people routinely change the hood to a microwave/hood combo. I always put microwaves on separate circuits so my suggestion to you is a separate circuit.