greenspark1
- New England
Hello,
I have several buildings that each have their own small 208/120V three phase generators. A typical building has a MDP which feeds the ATS and several other panels. The outdoor generator has a small built-in breaker which feeds the ATS, which then feeds an emergency panel EP nearby that is 100A main lugs only. This is not a required standby or emergency panel, just for prolonged winter outages- lights, some receptacles, boiler, etc.
My first question is if the ATS needs to have an OCPD to protect the load wiring. Otherwise you're relying on the upstream devices.
Second question is that there are some ATSs that are double lugged to EP1, EP2, EP3, etc (see photo). These don't have OCPD on the load side either and the EP panels are all MLO. I'm looking at 240.21(B)(1). Both the line and load side wires look about the same size, so that would comply with 240.21. Any other sections I should be looking to?
Third question- if the generator has an integrated breaker do you also need an external disconnect since it's an outside feeder? Seem a bit redundant, I'm not sure what purpose it serves. Thanks for any help!