ELECTRIC ACE
- Kemah, Texas
- Electric Contractor
What is the Smallest Natural (grounded conductor) for a service sized parallel 4 X 500 MCM Alu. ungrounded conductors?
That would be for the GEC. For the OP's question 220.61 comes into play.Doesnt table 250.66 drive that?
and if there is no or little neutral load, you apply 250.24(D)(2)For the OP's question 220.61 comes into play.
Which sends you to table 250.102(C)(1) which is very similar to 250.66.and if there is no or little neutral load, you apply 250.24(D)(2)
Yes, 250.102(C)(1) was added to get rid of confusion that was caused by using 250.66 for multiple purposes. Most notably the largest conductor required by 250.66 is 3/0 and 250.102(C)(1) requires conductors larger than 3/0.Which sends you to table 250.102(C)(1) which is very similar to 250.66.
Starting with the 2014 code, 250.24(C) has specifically referenced Table 250.102(C)(1) for the minimum size of the service grounded conductor.I'm Going with Table 250.66, 250 MCM Alu. one in each raceway.
I think it relates to service entrance conductors.
Table 250.102(C)(1) I think relates to bonding jumpers and Parallel feeders over 1750 to be sized at 12-1/2%.