Smallest Neutral (grounded conductor)

Smallest meaning that there is no neutral load?

Electric Ace, please update you profile to include your location and occupation.
 
Which sends you to table 250.102(C)(1) which is very similar to 250.66.
Yes, 250.102(C)(1) was added to get rid of confusion that was caused by using 250.66 for multiple purposes. Most notably the largest conductor required by 250.66 is 3/0 and 250.102(C)(1) requires conductors larger than 3/0.
 
I'm Going with Table 250.66, 250 MCM Alu. one in each raceway.
I think it relates to service entrance conductors.
Table 250.102(C)(1) I think relates to bonding jumpers and Parallel feeders over 1750 to be sized at 12-1/2%.
 
I'm Going with Table 250.66, 250 MCM Alu. one in each raceway.
I think it relates to service entrance conductors.
Table 250.102(C)(1) I think relates to bonding jumpers and Parallel feeders over 1750 to be sized at 12-1/2%.
Starting with the 2014 code, 250.24(C) has specifically referenced Table 250.102(C)(1) for the minimum size of the service grounded conductor.
 