IBC stipulates the smoke detector requirement for pressurized stairwells (note that the code excerpt below reads the detector must be in an "approved" location). There is a second part to 909.20.6 that stipulates if door closing devices are used, when they lose power or are activated by smoke detector, those conditions shall also activate ventilation equipment
NFPA 72 provides further direction on the detector location but bounces you around a few code excerpts while doing so. The end result when initiating action for a specific object or space is to locate the detector in close proximity to the object being protected. You'll learn something about elevator lobbies and ceiling heights reading this as well which can drive some elevator inspectors crazy.
IBC 2015 909.20.6 Ventilating Equipment: The activation of ventilating equipment required by the alternatives in Sections 909.20.4 and 909.20.5 (stair pressurization) shall be by smoke detectors installed at each floor level at an approved location at the entrance to the smoke proof enclosure.
NFPA 72 2013 17.4.10 If the intent is to initiate action when smoke/fire threatens a specific object or space, the detector shall be permitted to be installed in close proximity to that object or space.
NFPA 72 Annex A17.4.10 There are some applications that do not require full area protection, but do require detection, to initiate action when specific objects or spaces are threatened by smoke or fire, such as at elevator landings that have ceilings in excess of 15ft and for protection of fire alarm control units. In high ceiling areas, to achieve the desired initiation, such as for elevator recall and protection of fire alarm control units (FACUs), detection should be placed on the wall above and within 60 in from teh top of the elevator door(s) or FACU.
NFPA 72 21.3.5 A lobby smoke detector shall be located on the ceiling within 21ft of the centerline of each elevator door within the elevator bank under control of the detector
Exception: for lobby ceilin gconfigurations exceeding 15ft in height or that are other than flat and smooth, detector locations shall be determined in accordance with Chapter 17 (which gets us back to chapter 17 and some of the above applications)