FBarrera,
Take a look at the text below from NFPA 72
6.12.8 Suppression systems or groups of systems shall be controlled by a single control unit that monitors the associated initiating device(s), actuates the associated releasing device(s), and controls the associated agent release notification appliances. If the releasing control unit is located in a protected premises having a separate fire alarm system, it shall be monitored for alarm, supervisory, and trouble signals, but shall not be dependent on or affected by the operation or failure of the protected premises fire alarm system.
Exception: If the configuration of multiple control units is listed for releasing device service, and if a trouble condition or manual disconnect on either control unit causes a trouble or supervisory signal, the initiating devices on one control unit shall be permitted to actuate releasing devices on another control unit.