Re: Smoke Detectors and AFCI
Very good question. Here are three relevant articles:
- - - - - - - - - - - - - - - - - -
210.12(B):
Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.
- - - - - - - - - - - - - - - - - -
100 (Definitions):
Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
- - - - - - - - - - - - - - - - - -
210.3 Rating:
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits (my emphasis) shall be 15, 20, 30, 40, and 50 amperes.
- - - - - - - - - - - - - - - - - -
Please note that 210.12(B) does not speak of branch circuits that are rated at 15 or 20 amps. It speaks of outlets that are rated at 15 or 20 amps. So if you were to install an ?individual branch circuit? with a 10 amp breaker (210.3 allows this), and even if the branch circuit is thereby rated at 10 amps, you still do not alter the rating of the outlet. But an ?outlet? is defined in terms of a point in space. More practically, an outlet is a box into which you may install (for example) a receptacle, or onto which you may attach (for example) a ceiling light or a smoke detector.
But now I am out of my field, and need help. Is it true that the outlet boxes carry their own ratings? Can you buy an outlet box with a 20 amp rating? For if you run a branch circuit (that is rated at 10 amps) to the outlet box (that is rated 20 amps), and if you then attach a smoke detector to that box, then I believe that 210.12(B) would require AFCI protection. This is not because of the 10 amp branch circuit, but rather because of the 20 amp outlet.