I have a tech scratching his head (me too) and thought I might see if anyone here has had a similar problem and what is the fix.
We took a service call saying smoke detectors keep chirping. (system is BRK, 120 volt AC with 9 volt Backup) The tech assumed it was batteries, so he replaced them all. Problem didn't go away. So tech advises a detector is bad, replace all detectors. Did so and problem still exists. Tech calls me. I asked him to check voltages on red (signal) and neutral wires...50 volts!!! I told him to isolate the circuit to find where he was picking up the voltage. As he took apart the 9 detectors the voltage kept dropping by about an average 9 volts each opening, some openings didn't make a difference. So when he got them all apart, he has no voltage at any opening, once he starts putting the junctions (no detectors) back together, the voltage starts to climb again. Any ideas?
We took a service call saying smoke detectors keep chirping. (system is BRK, 120 volt AC with 9 volt Backup) The tech assumed it was batteries, so he replaced them all. Problem didn't go away. So tech advises a detector is bad, replace all detectors. Did so and problem still exists. Tech calls me. I asked him to check voltages on red (signal) and neutral wires...50 volts!!! I told him to isolate the circuit to find where he was picking up the voltage. As he took apart the 9 detectors the voltage kept dropping by about an average 9 volts each opening, some openings didn't make a difference. So when he got them all apart, he has no voltage at any opening, once he starts putting the junctions (no detectors) back together, the voltage starts to climb again. Any ideas?