I have an existing installation of smoke detectors in a suspended ceiling. The detectors are currently mounted directly to the ceiling tile. We are replacing the smoke detectors and the plan is to add a caddy bar/t-bar box hanger to attach the junction box and smoke detector from.
Does this assembly need to be supported independently of the ceiling grid, like shown in the picture below?
NEC 300.11(B) says "Cables and raceways shall not be supported by ceiling grids."
Since the junction box attached to the box hanger is not a raceway, I do not think we need the independent support wire. Thoughts?
Thanks in advance for your time and replies!
Does this assembly need to be supported independently of the ceiling grid, like shown in the picture below?
NEC 300.11(B) says "Cables and raceways shall not be supported by ceiling grids."
Since the junction box attached to the box hanger is not a raceway, I do not think we need the independent support wire. Thoughts?