Have you ever installed SD inside bathrooms?
not really, last couple months very slow, but I have like 3 aditions waiitng for approval, let's see what happens. Qre you in Essex too?
not really, last couple months very slow, but I have like 3 aditions waiitng for approval, let's see what happens. Qre you in Essex too?
Name-dropper! grinYes sir. Montclair, Verona, Cedar Grove, The Oranges, Maplewood areas.. and of course Newark ....:smile:
Yes.
Smoke detectors may be required in a bathroom, for that matter, one could be required anywhere/everywhere.
For example in a hospital for smoke damper control, the damper can be controled by a dedicated duct detector (which are prone to false alarms) or total area detection can be used to close the damper. The total area detection requires a smoke detector in every room fed by the HVAC system, including restroom/toilets.
Though NFPA 72 does state that smoke detectors shall not be installed in areas that are too extreme, so where there are showers the somke detectors may not want to be used due to false alarms (steam looks like smoke to the detector).
couldn't you install the ionization-type detector in this case?