I've got a 4 story, non-high rise private high school. The entire facility is sprinkled. This is in Mass, and per the E Catagory in the Mass Building Code, I'm telling a contractor that smoke detectors are not required in the facility at all. I'm not stating that this is the recommendation necessarily but strictly speaking the code doesn't require them.
I'm getting pushed back that in NFPA 72, any egress stairwell, requires smokes at the top and the bottom.
I know many of you can't comment on MA, but just your input on 72 would be helpful.
Thanks,
Mike
I'm getting pushed back that in NFPA 72, any egress stairwell, requires smokes at the top and the bottom.
I know many of you can't comment on MA, but just your input on 72 would be helpful.
Thanks,
Mike