Is there a violation to run a single thhn wire to interconnect smoke detectors. Situation is no way to run 14-3 between them but have 120 available in each room.
Why not use a wireless smoke, where you need 120 only @ one location ?
That would be a violation of 110.3(b), 300.3 and 310.13.
That would be a violation of 110.3(b), 300.3 and 310.13.
110.3(B) the manufacturer will tell you it is not designed for that use.
300.3(A) Single conductors specified in Table 310.13(A) shall only be installed where part of a recognized wiring method of chapter 3
310.13 These conductors shall be permitted for use in any of the wiring methods in any of the wiring methods recognized in chapter3 and as specified in their respective tables or elsewhere in this code.
If your going to consider it an article 725 installation I would say 725.31 would apply since at least in my state failure of the fire alarm sytem is considered a life safety hazzard and is grounds for revoking the certifacate of occupancy for a building.
INTERCONNECTING SMOKE ALARMS
? FOR INTERCONNECT LINE ONLY use #14-#18 AWG minimum
solid or stranded wire. When interconnecting, maximum wire
length between any two is 1,500 feet for #18 AWG or 4,000 feet
for #14 AWG (20 OHMS loop resistance).
? This smoke alarm may be interconnected with as many as 11
additional Firex model AD, ADC, PAD, FADC, and FPAD smoke
alarms, and/or as many as 6 Firex model ADH heat alarms for a
total of not more than 18 interconnected devices. DO NOT connect
to any type or model smoke alarm.
? Connect smoke alarms to a single AC branch circuit. If local
codes do not permit, be sure the neutral wire is common to
both phases.
The rest of the installation instructions do not address a single wire interconnect
In my opinion smoke alarms are not a fire alarm system.
• Connect smoke alarms to a single AC branch circuit. If local
codes do not permit, be sure the neutral wire is common to
both phases.
From here http://www.firexsafety.com/NR/rdonl...DB-124EB567BEB3/0/1101074CEnglish45804586.pdf
from Kidde\ firex
The smoke alarm must be installed to comply with all local codes having jurisdiction
in your area. All wiring shall be in accordance with articles 210 and 300.3(B) of
the US National Electrical Code, ANSI / NFPA 70 and NFPA 72. The multiple station
interconnect wiring must be in the same raceway as the AC power wiring
not sure it would help all that much in a retro fit or did I miss something ?The same fuse or circuit breaker must power all interconnected units