Smoke Detectors Under a Raised Floor

Status
Not open for further replies.

hforney500

Member
Location
New Jersey
One floor of my office building was previously used as an IT Equipment Room by the previous owner. The Air Conditioning Units which circulated cold air under the raised floor have been removed. This space is no longer used for enviormental air. The existing smoke detector panel for the detectors under the raised floor has also been removed. Am I correct that there is no longer a requirement for the smoke detectors.
 

bwyllie

Senior Member
Location
MA
Re: Smoke Detectors Under a Raised Floor

If there is wiring or any other combustible material under the raised floor then the smoke detectors would still be required.
 