Hi everyone. Working on a project with a raised floor area utilized as a plenum. Rooms are used for the electrical distribution equipment, NOT a data center covered by article 645.
I believe requirements for the smoke detectors inside a plenum are covered by 2024 NFPA 90A, a standard for the Installation of Air-Conditioning and Ventilating Systems. According to Chapter 8, Plenums; Paragraph 8.5, Raised Floor Plenums, section 8.5.5.10, smoke detectors are NOT required to meet the requirements of this section providing materials under raised floor are non-combustible and meet certain requirements.
Any thoughts on the subject?
Thank you.
I believe requirements for the smoke detectors inside a plenum are covered by 2024 NFPA 90A, a standard for the Installation of Air-Conditioning and Ventilating Systems. According to Chapter 8, Plenums; Paragraph 8.5, Raised Floor Plenums, section 8.5.5.10, smoke detectors are NOT required to meet the requirements of this section providing materials under raised floor are non-combustible and meet certain requirements.
Any thoughts on the subject?
Thank you.