smoke detectors

Status
Not open for further replies.

brantner

New member
In a resedental home how far away does a smoke detector have to be from the wall? Also how far from the peak of a valted ceiling? Where do they have to be located in a house used to take care of elderly people?
 

ryan_618

Senior Member
Re: smoke detectors

In a house the IRC doesn't adress vaulted ceilings or proximity to walls. If this house you speak of is for taking care of the elderly, you might not have a house, but rather an institution. I would check with the AHJ. If it is an institution, the NFPA 72 should govern locations.
 

earlydean

Senior Member
Re: smoke detectors

Every smoke detector comes with instructions. Follow them!
The International Building Code requires smoke detectors to be installed in accordance with NFPA 72.
NFPA 72, The National Fire Alarm Code, Section 5.7.1.9: "The location of smoke detectors shall be based on an evaluation of potential ambient sources of smoke, moisture, dust, or fumes, and electrical or mechanical influences to minimize nuisance alarms." and 5.7.1.11: "Detectors shall not be installed until after the construction cleanup of all trades is complete and final."

Looking at the installation instructions included with the detector, we find that all these concerns, plus the design of the ceiling, etc. is taken into consideration. Most of the detectors I've installed require a minimum clearance of 4-12" to the wall. (and ceiling for wall mounting) The theory is that smoke curls at corners, and would delay the activation of the detector if too close.
 

hbendillo

Senior Member
Location
South carolina
Re: smoke detectors

One of the appendices of NFPA 72 has some specific instructions for installing smoke detectors for these conditions. There is an illustration in the appendix that actually shows where to install the detector in a vaulted ceiling condition. You will also find an illustration that shows where not to install a detector in proximity to where the ceiling and the wall meet. Study the NFPA 72 and the applicable appendix and you should get most of you answers there. Are you working for and engineer to produce drawings? An engineer or someone licensed to design and issue fire alarm documents needs to be consulted.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: smoke detectors

In my area of work, the AHJ consider the dead air space to be six inches out from where the ceiling meets the wall. See: Minneapolis Smoke Detector Placement
The point, again, is to check with your local AHJ(s).