Hi!!!!! anyone have an idea!!! i'm installing smoke detectors that work on 24 volts, am i required to install 120 volt smoke detectors too ??????
Check your IRC. It states that in NEW installations the building wiring has to power the required smoke detectors and must have battery backup. If you choose to also put in 24V smoke detectors as well....thats your choice.
Check out IRC - R313.3 - Power Source
It depends on what, if any, fire code is enforced in your area. Most jurisdictions around me require 120 volt stand alone smoke detec...err....I mean alarms in addition to the 24 volt system detector.
If you install a listed 24 volt fire alarm system why would any jurisdiction require additional 120 volt alarms?
does it list a specific voltage? i don't ever remember the article saying it had to be 120v, or any voltage for that matter.
it has always been my understanding that low-voltage smoke detectors w/ a battery backup in the control panel meet the requirements because technically they are hard-wired, just to a low voltage transformer.
Ahhh, the joys of living in New Jersey, where our very own special edition of the IBC requires the detectors to perform the alarm function even if you rip the FACP off the wall. Hence, 120VAC interconnected smoke/heat/CO alarms even if you have a full blown FACP as well.
Ahhh, the joys of living in New Jersey, where our very own special edition of the IBC requires the detectors to perform the alarm function even if you rip the FACP off the wall. Hence, 120VAC interconnected smoke/heat/CO alarms even if you have a full blown FACP as well.
I'm just curious how you meet the supervision rule if there are over 12 connected, even if the supervision rule has been modified my understanding is that there isn't a manufacturer that makes a 120 volt smoke alarm that is listed over 12, at least thats what a rep from BRK told me.
There is, indeed, a deafening silence regarding "supervision" of these devices. Also, I believe the BRK rep is a teensy bit wrong in his assertion. What the directions with the detector say is identical to NFPA 72; the limitation is in the code, not the product.
You could do up to 64 devices, 42 of them smoke detectors if you could supervise them. Possibly as follows: Carefully install the devices as a Class B circuit, NO T-TAPPING! At the end of the circuit install a relay, such as a System Sensor PR-1 or throw up a 24VDC transformer and use an EOLR-1 and connect to a listed communicator such as a Silent Knight 5104B. If power on the circuit fails, the relay changes state and trips the communicator calling the central station and/or maybe ringing a local notification appliance. Cumbersome, but I think it meets the intent.
There is, indeed, a deafening silence regarding "supervision" of these devices. Also, I believe the BRK rep is a teensy bit wrong in his assertion. What the directions with the detector say is identical to NFPA 72; the limitation is in the code, not the product.
You could do up to 64 devices, 42 of them smoke detectors if you could supervise them. Possibly as follows: Carefully install the devices as a Class B circuit, NO T-TAPPING! At the end of the circuit install a relay, such as a System Sensor PR-1 or throw up a 24VDC transformer and use an EOLR-1 and connect to a listed communicator such as a Silent Knight 5104B. If power on the circuit fails, the relay changes state and trips the communicator calling the central station and/or maybe ringing a local notification appliance. Cumbersome, but I think it meets the intent.
So are your saying that there is a mfg out there that makes a LISTED smoke alarm that has been approved for 42 but because of the code it isn't allowed. What mfg. would that be?
... the detector plug alone would be enough to call it a t-tap...
If you remove a hard wired detector from its base and don't disconnect the module plug from the loop wire, the remaining detectors will continue to function. Hence, not T-tapped.