Default Smoke Detectors
* Where are smoke detectors required to be installed, and where do I find this information?
NFPA 72 and various building codes have different specific requirements.
Here is a rough summary of what Chapter 11 of NFPA 72 (specifically 11.5.1) requires:
* One in each bedroom (to wake people up).
* One on each level, including basement.
* A smoke in a basement shall be on the ceiling, near the entry to the stairs.
* One outside each sleeping area, within 21 feet of the door to any sleeping area. If the hallway is closed off from the sleeping and living areas by doors, then smokes are required on both the living and hallway sides of the door.
* When a door is installed in a stairway, smoke rising up the stairwell cannot be obstructed from a detector by the door.
* One in the living area of a guest suite.
* When a given level of a living area is 1000 sq.ft. or greater, one is required for every 500sq.ft. of floor area for that space, no greater than 30 ft apart.
* If a ceiling on any level has an elevation change of 24", each elevation needs one. Example: Vaulted living room on same floor as 8' ceiling for back hall, den, laundry.
* No closer than 3' to any cold air return or supply, or ceiling fan. Nuisance alarms due to dust attraction are common when this is done, and the sensitivity can diminish.
* No closer than 4" and no farther than 3' to peak of vaulted ceiling. Smoke rolls in corners, bypassing detector.
* No farther than 3' from peak of vaulted ceiling.
* No closer than 4" from wall on a flat ceiling.
* No closer than 4" from ceiling and no farther than 12", when wall mounted.
* Ambient temperature cannot exceed 100 F, or below 40 F, as in attics and garages.
* Interconnection of detectors is required.
* Per NEC 210.12, AFCI protection required. Per NFPA 72 11.6.3(7), if the smoke is supplied by an AFCI, then battery backup is required. By 11.6.4(1), the smoke must audibly report a low battery condition.
* The instruction booklet supplied with the smoke detector is required to be provided to the occupant. (72 11.8.4(1).)
* Smokes should be replaced every ten years. (72 11.8.5(b).)
Many smoke detectors come with instructions that mirror NFPA 72's requirements, so they could also be considered a 110.3(B) listing issue, if NFPA 72 has not been adopted in your area.
Here are some related threads, or you can search for the term "smoke detector" and find many results.
A free online viewable copy of NFPA 72, is available by clicking on this link (Click "I agree" to see the read-only document).
Thanks to Mark Henderson for the link and correction on the list above.
http://www.mikeholt.com/code_forum/s...ad.php?t=81410
http://www.mikeholt.com/code_forum/s...ad.php?t=78988
http://www.mikeholt.com/cgi-bin/code...755;p=1#000005
Smoke detector placement in dwellings - started 05/07. Includes quotes from the IRC and other building codes.
Last edited by George Stolz; 09-02-2007 at 12:41 PM.