Smoke Exhaust Fans

Status
Not open for further replies.

raven

Member
Can MC cable be used to feed Smoke Exhaust Fans or must conduit be used? I'm having trouble getting a finite answer to this.
Thanks
 
When you say "smoke exhaust" do you mean "smoke control" during a fire event, "smoke purge" after a fire event, or nuisance smoke removal for a process of some kind (cooking, machining, welding, etc)?
 
When you say "smoke exhaust" do you mean "smoke control" during a fire event, "smoke purge" after a fire event, or nuisance smoke removal for a process of some kind (cooking, machining, welding, etc)?

Can you answer to smoke control / smoke purge please?
 
Can you answer to smoke control / smoke purge please?

It will depend on jurisdiction, but smoke control usually requires 2-hour survivability (VitaLink cable or equal), while smoke purge can use less restrictive wiring methods (MC, RMC). Smoke control is a life-safety process, smoke purge is not.
 