I have an unfinished basement of a dormitory type building that has some hvac equipment such as boilers, heat exchangers and air handlers.

The ceiling height is about 8'.

I am not sure if it's more appropriate to install smoke or heat detectors.


Appreciate your input, thanks.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
..I am not sure if it's more appropriate to install smoke or heat detectors..

If fire code requires a smoke, Photoelectric may be preferred to Ionization type. Check fire Code may for Heat detectors in boiler rooms.

Fire code may also require Carbon Monoxide (CO) detectors for fuel-burning areas in a residential occupancy?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
If fire code requires a smoke, Photoelectric may be preferred to Ionization type. Check fire Code may for Heat detectors in boiler rooms.

Fire code may also require Carbon Monoxide (CO) detectors for fuel-burning areas in a residential occupancy?

Certainly check the code re smoke detector requirements, but try to stay away from smokes if possible for a utility/boiler room. If the boiler "coughs" on startup you may get a temporary smoke condition that leads to a visit from your friendly neighborhood fire department, who will be very cranky if they don't actually have a fire to fight. Even for heat detectors, you may want to use a conventional detector tied to a monitor module, said module located outside the boiler room footprint. Addressable devices have a UL listing limit of 100°F.
 