Smoke Purge

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
How does smoke purge relate to the electrical and fire alarm portion. My partial understanding is the fans exhaust the smoke out and dampers open or close(???). What is needed to be figured electrically and on the fire alarm side(control modules??)

Thanks.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
Depends on where this application is. We had a small indoor mall where if the fire was in the mall proper the mall exhausted and the suites went positive and if the fire was in one of the suites it was the oppisite.
 

ron

Senior Member
A big ticket item to be sure is picked up, is that if it is code required smoke control, that the control panel be listed as approved for smoke control. Many times it costs more than a regular fire alarm or building management control panel.
 