I inspector1966 Member Location Ada, Oklahoma Dec 7, 2010 #1 Is electrical nonmetallic tubing or smurf pipe, allowed by the 2005 NEC in Type V construction?
raider1 Senior Member Staff member Location Logan, Utah Dec 7, 2010 #2 Welcome to the forum. Take a look at 362.10 for uses permitted for ENT. Chris
I inspector1966 Member Location Ada, Oklahoma Dec 7, 2010 #3 smurf pipe thanks for the info. In my case, 362.12 (1) and Table 514.3(B)(1) are the answers that i was looking for.
smurf pipe thanks for the info. In my case, 362.12 (1) and Table 514.3(B)(1) are the answers that i was looking for.